Factory Mode
Mode Description:
Some devices may be shipped in a special mode called Factory mode. This mode is used typically for devices where their pre-configuration can cause unnecessary battery drain eg. during transportation, manipulation, or during storage. In this mode, the device is limited to very basic functionality with no heartbeats.
How to identify that a device is in Factory mode?
Short button press (SimplePack & SimplePack Plus) Magnet with reed switch interaction (SimpleIndustry & SimpleMeter) for 0 – 2.9 seconds.
The Factory mode presence is indicated by:
two long LED blinks
a message starting with FA30 is sent
How to exit Factory mode?
Long button press (SimplePack & SimplePack Plus) Magnet with reed switch interaction for (SimpleIndustry & SimpleMeter) for 3 – 5.9 seconds.
The Factory mode exit is indicated by:
rapid LED blinking for approx. 5 seconds
message starting with FAFA01
device reset into the pre-configured state.
There can be a specific setting to exit Factory mode automatically by timer overflow specified in API 6 registry E0 noted in SimpleTime.
For example, automatic Factory mode exit in 5 days after the device is manufactured if E0 is set to C5.
How to return to Factory mode?
In the case of a need to return to factory mode, you can write D5 with the value of 0x01 via downlink into API 6 registers. The Device will reboot into factory mode.
Payload Description
1st Byte = 0xFA = Factory mode
2nd Byte (Event)
The same rules as for any other event
- New Events:
0xF9 = Factory mode GAS message
0xFA = Factory mode exit message
0xFB = Factory mode ADC raw values
3rd – 12th Bytes
The same rules as for any other event (either appended payload or event-specific payload)
For the new events:
Event 0xF9
3rd and 4th Byte is the Gas value in ppm
Event 0xFA
3rd Byte = Type of exit
0x00 = enter
0x01 = exit via button
0x02 = exit via timer
0x03 = exit via register 0xD5 mf bit
4th – 7th Bytes = ID of the device
Event 0xFB
3rd Byte = ADC A mV MSB
4th Byte = ADC A mV LSB + MS 4bit ADC B
5th Byte = ADC B mV LSB
Examples
FA30 = Short press in Factory mode
FA30C0307D = Short press in Factory mode with Voltage (3.0 V) and Temperature (22.5 °C) appended to the payload
FAFA01025B46E2 = Exit of Factory mode via button and with the ID of the device (025B46E2)